I'm trying to integrate the Deltaohm HD3910 sensor, which I bought with Modbus communication. Here attached u can see some screenshots of Loxone Config setup and the DataSheet of the HD3910.
I'm not able to get the values out of it... I always see 0 from all 3 registers available.
- I've left the sensor attached to the Loxone 24Vdc and connected the Modbus wires to a usb-Modbus converter, using ModbusDoctorV2 application on the PC: from here everything works just fine, same speed and parameters (Address 05H, 9600, 8-n-1) I've used with Loxone Modbus extension.
- Since I also have other 2 devices connected to the Modbus extension, and they're working fine. I've double checked the Address and they're 1, 2, 5.
- I've terminated the last device with a 120R.
I really don't know what else I can do here... on Config there's no helpful monitor, and I don't want to go ahead using a Modbus protocol analyzer...
Thanks!