    Comfort cooling maxed at 26C?

    Hello,
    In one specific room, I prefer not to use air conditioning unless it gets really hot, especially since the sensors seem to be reading temperatures a bit too high. I’m trying to set the "comfort cooling" to around 27°C, but the maximum I can adjust it to is 26°C. What’s going on? Is this limit fixed, or does it relate to other cooling settings? (Currently, Eco is set to 29°C.)
  • Jan W.
    Lox Guru
    • 30.08.2015
    • 1489

    #2
    There is no limit, but dependencies. You may have to increase the limit for heat protection in expert settings first before you can increase "comfort cooling". "Eco" should be a delta, e.g. 2 degrees and it acts as an increase for "eco cooling" and a decrease for "eco heating".