In one specific room, I prefer not to use air conditioning unless it gets really hot, especially since the sensors seem to be reading temperatures a bit too high. I’m trying to set the "comfort cooling" to around 27°C, but the maximum I can adjust it to is 26°C. What’s going on? Is this limit fixed, or does it relate to other cooling settings? (Currently, Eco is set to 29°C.)
Comfort cooling maxed at 26C?
Einklappen
X
-
Comfort cooling maxed at 26C?
Hello,
In one specific room, I prefer not to use air conditioning unless it gets really hot, especially since the sensors seem to be reading temperatures a bit too high. I’m trying to set the "comfort cooling" to around 27°C, but the maximum I can adjust it to is 26°C. What’s going on? Is this limit fixed, or does it relate to other cooling settings? (Currently, Eco is set to 29°C.)Stichworte: - -
There is no limit, but dependencies. You may have to increase the limit for heat protection in expert settings first before you can increase "comfort cooling". "Eco" should be a delta, e.g. 2 degrees and it acts as an increase for "eco cooling" and a decrease for "eco heating".Miniserver v14.5.12.7, 2x Ext., 2x Relay Ext., 2x Dimmer Ext., DMX Ext., 1-Wire Ext., Gira KNX Tastsensor 3 Komfort, Gira KNX Präsenzmelder, Fenster- und Türkontakte, Loxone Regen- und Windsensor, Gira Dual Q Rauchmelder vernetzt, 1x Relais-Modul