Each chain winder has a cable with 4 wires -
1. Neutral
2. Close
3. Open
4. Earth
Internally, each winder has a complex circuit board with transformer and sensing for end positions and throw.
I have made the attached circuit and thought it would work in theory. The basic premise is that the direction is set by an external double throw relay, and the winder to run is switched with the neutral through a Loxone single throw relay. The anticipated limitation with this is that only one direction (open or close) can be actioned at any given time across all the winders. This is acceptable.
In practice, it doesn't work when more than 1 chain winder is installed.
In the attached circuit, both winders work successfully when connected individually. If they are both wired up, neither works. I think I have established the cause as some sort of 'back EMF' that causes protection circuits to shut-down the motors.
ie. When the Open Bus is energised, there's current flow through the connected Close Bus to the other motor. The internal protection circuits are (presumed) to protect for the possibility of voltage at both Open and Close.
Has anyone used these types of AC winders with less than 2 Loxone relays per device?
Kommentar